Bonding Extraneous Conductive Parts | on ElectriciansForums (2024)

Discuss Bonding Extraneous Conductive Parts in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

J

John-

-
Joined
Jan 13, 2019
Messages
196
Reaction score
48
Location
Uk
  • Jan 13, 2019
  • #1

hi. Question re bonding a metal where cold comes in as metal pipe ground into house. So cold will be bonded where service comes in. Read article in wiring matters 2019 about changes for part 18. Example given of faulty kettle where fault to earth exists at kettle, some one touches kettle earth and metal tap, pipe should be same so neggligeable difference exhists and no shock. Just made me think for a bit...

Questions...

Why didn’t the fuse or circuit protective device operate leaving no touch voltage?
I assume above is because current not high enough to rupture, leaving a potential high enough to kill but not high enough to damage cable- assumes rcd not used... which is wrong in itself given the example, but let’s go by their example.

So really when we are bonding like this aren’t we suplimenting the supplied earth into the building with the general mass of earth and not the other way. round? For the example above to be dangerous the General Mass of Earth has to be of an impedance lower than the earth connected to the kettle. Otherwise the fault current would not flow with no touch voltage.

So this means then that GME is lower than supplied cable and when you do you EFLI testing you should disconnect all bonds, otherwise the reading will include a supply pipe as an earth path that could change if it is converted to plastic which could then mean the overall ZS is increased, increasing disconnection times.

Thoughts?

telectrix

-

Mentor

Arms

Joined
Sep 5, 2010
Messages
73,534
Reaction score
67,276
Location
cheshire/staffordshire
  • Jan 13, 2019
  • #2

the purpose of main bonding is to raise the potential of extraneous metalwork ( e.g. water pipes) to the 230V for the duration of the fault current. i.e. until the appropriate OCPD reacts.

telectrix

-

Mentor

Arms

Joined
Sep 5, 2010
Messages
73,534
Reaction score
67,276
Location
cheshire/staffordshire
  • Jan 13, 2019
  • #3

why the dislike, pete?

Pete999

-

Arms

Joined
Mar 14, 2013
Messages
25,946
Reaction score
17,089
Location
Northampton
  • Jan 13, 2019
  • #4

telectrix said:

why the dislike, pete?

Sausage fingers Tel meant to be a like Apologies for the error, hope I didn't offend.

telectrix

-

Mentor

Arms

Joined
Sep 5, 2010
Messages
73,534
Reaction score
67,276
Location
cheshire/staffordshire
  • Jan 13, 2019
  • #5

thought as much. no offence taken. can you undo?

Pete999

-

Arms

Joined
Mar 14, 2013
Messages
25,946
Reaction score
17,089
Location
Northampton
  • Jan 13, 2019
  • #6

J

johnduffell

-

Esteemed

Joined
Jun 13, 2015
Messages
693
Reaction score
479
Location
uk
  • Jan 13, 2019
  • #7

telectrix said:

the purpose of main bonding is to raise the potential of extraneous metalwork ( e.g. water pipes) to the 230V for the duration of the fault current. i.e. until the appropriate OCPD reacts.

That's one effect but the high level purpose is to create an equipotential zone which is basically preventing any potentially accessible conductive item introducing a different (from the installation earth) potential into the zone.

telectrix

-

Mentor

Arms

Joined
Sep 5, 2010
Messages
73,534
Reaction score
67,276
Location
cheshire/staffordshire
  • Jan 13, 2019
  • #8

johnduffell said:

That's one effect but the high level purpose is to create an equipotential zone which is basically preventing any potentially accessible conductive item introducing a different (from the installation earth) potential into the zone.

agreed. both exposed conductive parts and extraneous parts are equipotential, so when an exposed part rises in voltage due to a fault, the extraneous parts rise the same.

Midwest

-

Nearly Esteemed

Arms

Joined
Mar 21, 2011
Messages
13,314
Reaction score
10,625
Location
Oxfordshire
  • Jan 13, 2019
  • #9

telectrix said:

thought as much. no offence taken. can you undo?

Least it wasn't a dumb. Bonding Extraneous Conductive Parts | on ElectriciansForums (8)

D

Deleted member 26818

  • Jan 13, 2019
  • #10

What happens when the tap and bonding conductor has a resistance lower than the R2 of the socket circuit the kettle is plugged into?

telectrix

-

Mentor

Arms

Joined
Sep 5, 2010
Messages
73,534
Reaction score
67,276
Location
cheshire/staffordshire
  • Jan 13, 2019
  • #11

spinlondon said:

What happens when the tap and bonding conductor has a resistance lower than the R2 of the socket circuit the kettle is plugged into?

then you hope that the touch voltage is <50V.

J

johnduffell

-

Esteemed

Joined
Jun 13, 2015
Messages
693
Reaction score
479
Location
uk
  • Jan 13, 2019
  • #12

spinlondon said:

What happens when the tap and bonding conductor has a resistance lower than the R2 of the socket circuit the kettle is plugged into?

the fault disconnection time would be <400ms so it's deemed to be OK for that time.
But you are spot on and you illustrate exactly why supplementary bonding is essential in bathrooms - to remove the resistance between MET and the appliance CPC termination.
The only way around that is to have RCD protection on all circuits serving the bathroom which is a requirement for new installs anyway hence supplementary bonding going the way of the dodo.

D

Deleted member 26818

  • Jan 13, 2019
  • #13

johnduffell said:

the fault disconnection time would be <400ms so it's deemed to be OK for that time.
But you are spot on and you illustrate exactly why supplementary bonding is essential in bathrooms - to remove the resistance between MET and the appliance CPC termination.
The only way around that is to have RCD protection on all circuits serving the bathroom which is a requirement for new installs anyway hence supplementary bonding going the way of the dodo.

How does that work if for instance the fault current comes into the location via the pipework?

Wilko

-

Arms

Joined
Jul 28, 2016
Messages
6,245
Reaction score
6,529
Location
Berkshire
  • Jan 13, 2019
  • #14

spinlondon said:

How does that work if for instance the fault current comes into the location via the pipework?

Interesting, but how could that be? (if the pipes are bonded to MET at entry to the Building...)

D

Deleted member 26818

  • Jan 13, 2019
  • #15

Wilko said:

Interesting, but how could that be? (if the pipes are bonded to MET at entry to the Building...)

What if the incoming supplies are plastic?

Reply to Bonding Extraneous Conductive Parts in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar threads

  • Question

UKBonding of extraneous conductive frame

Why would the RCD fail … yes it can happen but then it may not.Without it you have no protection on the TT System

  • Tequila
  • UK Electrical Forum
  • 36
  • 4K

23

  • bondingconductiveextraneousframe
Replies
36
Views
4K

Dec 29, 2023

cliffed

S

Earthing roof beams and roofing sheets on an attached garage.

Not really its clear in black and white. Not knowing the regs isnt the regs books fault.

  • spantheman
  • The Welcome Forum
  • 10
  • 791
  • bondinggaragesystem
Replies
10
Views
791

Aug 26, 2024

bigspark17

Bonding Extraneous Conductive Parts |  on ElectriciansForums (2024)
Top Articles
Latest Posts
Recommended Articles
Article information

Author: Rob Wisoky

Last Updated:

Views: 6441

Rating: 4.8 / 5 (48 voted)

Reviews: 95% of readers found this page helpful

Author information

Name: Rob Wisoky

Birthday: 1994-09-30

Address: 5789 Michel Vista, West Domenic, OR 80464-9452

Phone: +97313824072371

Job: Education Orchestrator

Hobby: Lockpicking, Crocheting, Baton twirling, Video gaming, Jogging, Whittling, Model building

Introduction: My name is Rob Wisoky, I am a smiling, helpful, encouraging, zealous, energetic, faithful, fantastic person who loves writing and wants to share my knowledge and understanding with you.